In a three-phase circuit with V_L = 480 V, I_L = 30 A, cosφ = 0.8, what is the real power P?

Prepare for the REC Electrical Module Test. Enhance your understanding with detailed questions, comprehensive hints, and thorough explanations. Boost your readiness and confidence for the actual exam!

Multiple Choice

In a three-phase circuit with V_L = 480 V, I_L = 30 A, cosφ = 0.8, what is the real power P?

Explanation:
Real power in a three-phase circuit is the portion of the apparent power that does useful work. For a balanced system, P = √3 V_L I_L cosφ, where V_L is the line-to-line voltage, I_L is the line current, and cosφ is the power factor. With V_L = 480 V, I_L = 30 A, and cosφ = 0.8, P ≈ 1.732 × 480 × 30 × 0.8. First 480 × 30 = 14,400; times 0.8 gives 11,520; then 11,520 × 1.732 ≈ 19,953 W, or about 19.95 kW. This is essentially 19.94 kW, matching the given value.

Real power in a three-phase circuit is the portion of the apparent power that does useful work. For a balanced system, P = √3 V_L I_L cosφ, where V_L is the line-to-line voltage, I_L is the line current, and cosφ is the power factor. With V_L = 480 V, I_L = 30 A, and cosφ = 0.8, P ≈ 1.732 × 480 × 30 × 0.8. First 480 × 30 = 14,400; times 0.8 gives 11,520; then 11,520 × 1.732 ≈ 19,953 W, or about 19.95 kW. This is essentially 19.94 kW, matching the given value.