In a three-phase circuit with line current I_L = 50 A, line voltage V_L = 480 V, and power factor cosφ = 0.9, what is the real power P?

Prepare for the REC Electrical Module Test. Enhance your understanding with detailed questions, comprehensive hints, and thorough explanations. Boost your readiness and confidence for the actual exam!

Multiple Choice

In a three-phase circuit with line current I_L = 50 A, line voltage V_L = 480 V, and power factor cosφ = 0.9, what is the real power P?

Explanation:
In a balanced three-phase circuit, the real power is found from P = √3 × V_L × I_L × cosφ. This combines the line voltage, line current, and how effectively the power is used (power factor). Substituting the values: √3 ≈ 1.732, V_L = 480 V, I_L = 50 A, cosφ = 0.9 gives P ≈ 1.732 × 480 × 50 × 0.9. First, 1.732 × 480 ≈ 831.36; then 831.36 × 50 = 41,568; finally 41,568 × 0.9 ≈ 37,411 W, or about 37.41 kW. Rounding may yield values near 37.32–37.41 kW, so the result is about 37.4 kW, aligning with the given answer when rounded.

In a balanced three-phase circuit, the real power is found from P = √3 × V_L × I_L × cosφ. This combines the line voltage, line current, and how effectively the power is used (power factor). Substituting the values: √3 ≈ 1.732, V_L = 480 V, I_L = 50 A, cosφ = 0.9 gives P ≈ 1.732 × 480 × 50 × 0.9. First, 1.732 × 480 ≈ 831.36; then 831.36 × 50 = 41,568; finally 41,568 × 0.9 ≈ 37,411 W, or about 37.41 kW. Rounding may yield values near 37.32–37.41 kW, so the result is about 37.4 kW, aligning with the given answer when rounded.